I have a multi-family apartment project where inside each unit will be a mechanical closet to house a gas water heater and gas air handler. Where in the code do I need to look to determine the required fire rating of the walls, floor, and ceiling of the mechanical closet?
 
There is no requirement for fire ratings. However, there are requirements for clearances when adjacent to combustible construction, that typically require compliance with the manufacturer's instructions.
 
There is no requirement for fire ratings. However, there are requirements for clearances when adjacent to combustible construction, that typically require compliance with the manufacturer's instructions.
I don't think the mechanical closet would fall under incidental uses, but if it did, then that is where the required wall rating would be found, correct?
 
I don't think the mechanical closet would fall under incidental uses, but if it did, then that is where the required wall rating would be found, correct?
You would need about a 10,000 sq. ft. apartment to require a furnace that would need protection per the incidental use requirements. But even then, since a Group R requires sprinkler protection, the sprinkler system would negate the need for fire-resistive construction.
 
You would need about a 10,000 sq. ft. apartment to require a furnace that would need protection per the incidental use requirements. But even then, since a Group R requires sprinkler protection, the sprinkler system would negate the need for fire-resistive construction.
Thanks!
 