Required receptacles on wallspace with a pocket door

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
Here is the scenario to ponder:

If you had an existing building level 2 renovation for a dwelling unit in a high rise with post-tension slabs that created wallspace for a pocket door which now would required a receptacle now that there is wall space 24" or greater, is there a product or method available to install a required receptacle?
 
One method would be making the wall where the pocket door is located a little thicker with additional framing in order to accommodate the required receptacle box depth.

If that is not possible, is there a product? How do you ensure wiring will stay secured and out of the way of the sliding pocket door?
 
If that is not possible, is there a product? How do you ensure wiring will stay secured and out of the way of the sliding pocket door?

Not my problem....Wall space is wall space. The PD cavity shouldn't be longer than 4' which would give you 24" of existing wall to work with too...
 
ivory-wiremold-legrand-raceway-accessories-nm2-d-4f_1000.jpg
 
PocketDoor-Electrical2.jpg


Shallow switch boxes installed in a pocket door frame, looks like it needs a metal guard to protect the 14g romex wiring, but looks doable. Get "er" done!
 