Getting confused here, received RESCheck report and I noticed on the Inspectors Check List that the insulation for the duct work located outside the building envelope is suppose to be R8 for all supply and R6 for all others. It is not noted on the plans or any where else in the RESCheck report that the ducts need to be insulate. Can I assume that if it is noted on the inspection checklist that it must conform to those requirements? The confusion I see is that the 2012 IECC states insulating the duct work is listed as prescriptive and the RESCheck is a Total Building Trade-Off. Thanks in advance for the help