ICE ... here is the reference. Sorry. I didn't see that you had repeated your request.
Do you see 440.13 as a comprehensive list or can I just add a plug to my compressor/condenser and change my non-fused disconnect to an outdoor outlet and cover? Even based on this short list ... moveability (wheels, attachment, etc) and amperage don't seem to be limiting factors. Those big built-in refrigerators probably weigh more than my condenser and some room air conditioners (mini-split systems and some window units) draw more than a 110v/20a circuit can provide.
The problem is that in all honesty, no one thinks that a non-fused disconnect is more likely to be repaired or replaced while the circuit is energized than the repair/replacement of a regular outlet. In fact, an A/C disconnect is probably much less likely to undergo repair/replacement while energized. I've seen lots of guys "take a chance" on a repair with an energized110v/20a circuit and none "take a chance" with an energized 220v/50a circuit.
So has no one just put a plug on their compressor? I don't think it is the best way to do things, but it seems to meet the rules.
----------------------------------------------------------------------------------------------
For cord-connected
equipment such as room air conditioners, household refrigerators and freezers, drinking water coolers, and beverage dispensers, a separable
connector or an
attachment plug and
receptacle shall be permitted to serve as the
disconnecting means.
Informational Note: See
440.63 for room air conditioners.
Diagram
Disconnecting means shall be located within sight from, and
readily accessible from, the air-conditioning or refrigerating
equipment. The
disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating
equipment.
Disconnecting means shall meet the working
space requirements of
110.26(A).
The
disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration
equipment or where it obscures the
equipment nameplate(s).
Exception No. 1: Where the disconnecting means provided in accordance with 430.102(A) is lockable in accordance with 110.25 and the refrigerating or air-conditioning equipment is essential to an industrial process in a facility with written safety procedures, and where the conditions of maintenance and supervision ensure that only qualified persons service the equipment, a disconnecting means within sight from the equipment shall not be required.
Exception No. 2: Where an attachment plug and receptacle serve as the disconnecting means in accordance with 440.13, their location shall be accessible but shall not be required to be readily accessible.