So here is what 110.26 says:
(A) Working Space
Working
space for
equipment operating at 1000 volts, nominal, or less to
ground and likely to require examination, adjustment,
servicing, or maintenance while
energized shall comply with the dimensions of
110.26(A)(1), (A)(2), (A)(3), and (A)(4) or as required or permitted elsewhere in this
Code.
Definition for equipment from Ch 1:
Equipment. A general term, including
fittings,
devices,
appliances,
luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
Definition of a Receptacle
Receptacle. A contact
device installed at the
outlet for the connection of an
attachment plug, or for the direct connection of electrical
utilization equipment designed to mate with the corresponding contact
device. A single
receptacle is a single contact
device with no other contact
device on the same yoke or strap. A multiple
receptacle is two or more contact
devices on the same yoke or strap.
Note the word "device" in both definitions
With these definitions in mind, can you walk me through how you test a GFCI outlet in a kitchen or bathroom without power? If not or if not done routinely, can you walk me through how those receptacles that are on the wall behind the counter and under the overhang of cabinets meet 110.26A?
I bring this up because I don't see how a non-fused disconnect for an A/C condenser needs any more power on "examination, adjustment, servicing, or maintenance" than a regular receptacle (it actually requires less due to the GFCI testing issue raised above). In fact, now that I am looking at it, a non-fused disconnect meets the definition of a receptacle.
How would we rectify this discrepancy where every receptacle requires 110.26A work space requirements? Maybe we could consider non-fused disconnects to be "receptacles" and exempt "receptacles" from the work-space requirement all-together. In any case, I hope the inspectors on this forum don't go failing every one of your inspections due to receptacles (aka electrical equipment which includes devices which includes receptacles) not meeting the work space requirements. jar546 the snarky me says that people are just too lazy to put pop-up plugs every two feet within 6" of the front edge of their countertops to be in compliance.