Residential Construction Type

Stephen Bent

REGISTERED
Joined
Dec 13, 2017
Messages
3
Location
Springfield, MO
I am currently designing a two story with basement 8,200 sq. ft. ICF construction residence with insulated concrete floors and manufactured wood truss roof system. I am trying to determine what the IBC construction type would be for this type of building.
 
Section 602 and Table 601 should give you some guidance. Type VB is a safe and easy call, but if it is single family why not use the IRC? No 'construction type' to worry about and prescriptive provisions for ICF (good call BTW, my basement is ICF and I'm glad I did it).
 
Agree with JBI, if you're using IRC then the question really doesn't come up, if you're using IBC then VB is a safe call. You could use a more restrictive type if you want, but there should be no reason to.
 
Welcome to the forum Mr. Bent.

IRC would be appropriate up to 3 stories above grade for any materials permitted by the code.

Under the IBC with the wood roof truss narrows it down to Type 3 (III) or 5 (V). The issue for Type 3 requires a 2-hr. fire-resistant construction of the exterior load bearing walls in accordance with Table 601.

Note need to follow the approved manufacturer's installation guidelines such as an ICC ESR for Type 3 to assure its installation is compliant as noncombustible

The concrete floor would allow it be Type 2 (II) provided the wood roof assembly is of FRTW or meets another exception in 603.1
 