I am doing some IECC CEUs, and the training and code book say one thing, but the practice quiz says another. Section M1505 is directly related to the IECC training. Here is the situation.
There are two options under M1505.4.3 for Mechanical Ventilation Rate. You can use Table M1505.4.3(1), or you can use Equation 15-1. That is clear, cut and dry. Here is the problem. The exception allows the ventilation fan to run as low as 25% of the time. However, you have to use Table M1505.4.3(2) to adjust the required CFM. Again, easy no problem. Here is where the confusion comes in.
If you are not going to use a continuous fan, and want to go intermittent, can you use Table M1505.4.3(2) for the number based on Table M1505.4.3(1) only or could you use the same factor table if you choose to use Equation 15-1?
The way it was taught was that the factor is always multiplied by the table, not the equation, but one of the questions could only be answered correctly if you used the equation to multiply by the factor.
There are two options under M1505.4.3 for Mechanical Ventilation Rate. You can use Table M1505.4.3(1), or you can use Equation 15-1. That is clear, cut and dry. Here is the problem. The exception allows the ventilation fan to run as low as 25% of the time. However, you have to use Table M1505.4.3(2) to adjust the required CFM. Again, easy no problem. Here is where the confusion comes in.
If you are not going to use a continuous fan, and want to go intermittent, can you use Table M1505.4.3(2) for the number based on Table M1505.4.3(1) only or could you use the same factor table if you choose to use Equation 15-1?
The way it was taught was that the factor is always multiplied by the table, not the equation, but one of the questions could only be answered correctly if you used the equation to multiply by the factor.