I'm preparing a short class for design students about Residential placement of smoke detectors -the basics
It includes both R-2 & R-3 groups.
R-2 specific to multi-units in a building (condos)
In my practice, I have always placed them inside/outside bedrooms and if the dwelling is one story, that is typically sufficient to satisfy the one per story requirement, and this has never been an issue with the AHJ.
However, now that I need to reference chapter and verse for the class, I noticed the very slight difference between IBC and IRC, particularly # 3.
IBC 907.2.10.2 (2018)
Single or multiple-station smoke alarms shall be installed and maintained in Groups R-2, R-3, R-4 and I-1 regardless of occupant load at all of the following locations:
IRC 314.3
Smoke alarms shall be installed in the following locations:
)
Basically, I've been following the IRC for everything.
For reference: most of my work is new commercial or tenant fit ups & single family homes, but not a lot of residential renovations in the R2 category that fall under the IBC.
Thank you!
I'm preparing a short class for design students about Residential placement of smoke detectors -the basics
It includes both R-2 & R-3 groups.
R-2 specific to multi-units in a building (condos)
In my practice, I have always placed them inside/outside bedrooms and if the dwelling is one story, that is typically sufficient to satisfy the one per story requirement, and this has never been an issue with the AHJ.
However, now that I need to reference chapter and verse for the class, I noticed the very slight difference between IBC and IRC, particularly # 3.
IBC 907.2.10.2 (2018)
Single or multiple-station smoke alarms shall be installed and maintained in Groups R-2, R-3, R-4 and I-1 regardless of occupant load at all of the following locations:
- On the ceiling or wall outside of each separate sleeping area in the immediate vicinity of bedrooms.
- In each room used for sleeping purposes.
- In each story within a dwelling unit, including basements but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level.
IRC 314.3
Smoke alarms shall be installed in the following locations:
- In each sleeping room.
- Outside each separate sleeping area in the immediate vicinity of the bedrooms.
- On each additional story of the dwelling, including basements and habitable attics and not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level.

Basically, I've been following the IRC for everything.
For reference: most of my work is new commercial or tenant fit ups & single family homes, but not a lot of residential renovations in the R2 category that fall under the IBC.
Thank you!