• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Rock wool insulation as fire block

alaskajoe

Registered User
Joined
May 22, 2019
Messages
53
Location
Alaska
Can you use rock wool insulation in a 2 x 4 stud cavity from first floor through top plate on second floor in balloon framing. Older home remodel
 
I find one mention of rock wool and two of mineral wool in the residential code. I don't know that rock wool is an insulation. At least I have not seen it being used as an insulation.

R302.4.2 Membrane penetrations. Membrane penetrations shall comply with Section R302.4.1. Where walls are required to have a fire-resistance rating, recessed fixtures shall be installed so that the required fire-resistance rating will not be reduced.

Exceptions:
1. Membrane penetrations of not more than 2-hour fire-resistance-rated walls and partitions by steel electrical boxes that do not exceed 16 square inches (0.0103 m2) in area provided that the aggregate area of the openings through the membrane does not exceed 100 square inches (0.0645 m2) in any 100 square feet (9.29 m2) of wall area. The annular space between the wall membrane and the box shall not exceed 1/8 inch (3.1 mm). Such boxes on opposite sides of the wall shall be separated by one of the following:

1.2 By a horizontal distance of not less than the depth of the wall cavity where the wall cavity is filled with cellulose loose-fill, rockwool or slag mineral wool insulation.

R302.11.1 Fireblocking materials. Except as provided in Section R302.11, Item 4, fireblocking shall consist of the following materials.

1. Two-inch (51 mm) nominal lumber.

2. Two thicknesses of 1-inch (25.4 mm) nominal lumber with broken lap joints.

3. One thickness of 23/32-inch (18.3 mm) wood structural panels with joints backed by /32-inch (18.3mm) wood structural panels.

4. One thickness of 3/4-inch (19.1 mm) particleboard with joints backed by 3/4-inch (19.1 mm) particle- board.

5. One-half-inch (12.7 mm) gypsum board.

6. One-quarter-inch (6.4 mm) cement-based millboard.

7. Batts or blankets of mineral wool or glass fiber or other approved materials installed in such a manner as to be securely retained in place.

8. Cellulose insulation installed as tested in accordance with ASTM E119 or UL 263, for the specific appli- cation.
 
The rock wool insulation I have seen has been in century old attics, and is similar to a handful of eggs. Can't imagine how it could be supported in a stud cavity to meet the requirements.
 
I am looking at R302.1.1.1(2012) and to me it appears you can.They are using rock wool or Roxul a lot here in Alaska now. It is dense and friction fits wonderfully. It does not slip in the wall or floor cavity at all. Bugger to cut but is quite effective and has sound deadening qualities also.
Someone in an old house remodel want to fill stud cavities with batts of Roxul.
 
I see Rockwool used in a project at least once a month. Residential basement finishes being its top use, old home remodel being second and additions being its third use. I’ve seen it used in minimal commercial application. You can also use it to protect TJI joists.
Rockwool does not retain water, water does not penetration Rockwool like typical fiberglass insulation along with the fire advantage.

As alaskajoe states, friction fit and is available in 16” or 24” wide cavities.
 
So in response to my original question under R302.11.1 (7) (2012 IRC) it would be allowed as a fireblock
 