Roll in shower part of turning space

I seen roll-in showers with no lip at all. And it work as part of the circular turning space.

ANSI 2009 section 304.2 turning space Floor Surface. Floor surfaces of a turning space shall comply with Section 302. Changes in level are not permitted within the turning space.

EXCEPTION: Slopes not steeper than 1:48 shall be permitted.

So if there is no lip and the slope toward the drain is less than 1:48 could it be part of the turning space?
 
Rick18071 said:
I seen roll-in showers with no lip at all. And it work as part of the circular turning space.ANSI 2009 section 304.2 turning space Floor Surface. Floor surfaces of a turning space shall comply with Section 302. Changes in level are not permitted within the turning space.

EXCEPTION: Slopes not steeper than 1:48 shall be permitted.

So if there is no lip and the slope toward the drain is less than 1:48 could it be part of the turning space?
you are correct rick

ICC A117.1-2009

301.2 Overlap.

Unless otherwise specified, clear floor

spaces, clearances at fixtures, maneuvering clearances

at doors, and turning spaces shall be permitted to overlap

304.2 Floor Surface. Floor surfaces of a turning space

shall comply with Section 302. Changes in level are not

permitted within the turning space.

EXCEPTION: Slopes not steeper than 1 :48 shall be

permitted.
 