I did a search and couldn't find anything, so if there's a thread answering this, please direct me!
VB building with 5 feet of fire separation distance. Wood trusses and no parapet. Designer wants to put 1-hour on the ceiling and call it good. Is that okay? We are looking at 705.11, exception 4. Occupancy Classification is S-1.
I am not sure if that is sufficient, because Section 705.5 says that walls with less than five feet of fire separation distance must be rated from both sides. Does this include roof/ceilings as well as walls?
This is a commercial building, but I keep thinking of IRC Section R302.2.2--the exception--where a parapet is not required if there are fire-resistant materials applied to the roof decking, or the roof decking is non-combustible, and in both cases there is a minimum class C roofing. Is there a counterpart to this informaion in the IBC? The IBC commentary to Section 705.11 was no help either.
Is protecting the ceiling equivalent?? That would seem to me to be protecting from the inside, but as I asked above, does 705.5 apply to roof/ceilings?
Also, does it matter that the terminology in exception 4 is different than exception 3? Exception 3 says "roofs of...fire-resistance-rated construction," and exception 4 says "roof/ceiling framing elements...shall be of...fire-resistive-rated construction." I took out part of the sentances so you can see the parts I'm focused on.
Section 711 (horizontal assemblies) did not help. I didn't expect to find help in Chapter 15, but looked just in case, and it only covers fire classification as expected. The gypsum manual has assemblies for wood trusses, but they are all just showing ceiling protection, and nothing on the roof.
I also need to address the 1-ft overhang, but one thing at a time!!
VB building with 5 feet of fire separation distance. Wood trusses and no parapet. Designer wants to put 1-hour on the ceiling and call it good. Is that okay? We are looking at 705.11, exception 4. Occupancy Classification is S-1.
I am not sure if that is sufficient, because Section 705.5 says that walls with less than five feet of fire separation distance must be rated from both sides. Does this include roof/ceilings as well as walls?
This is a commercial building, but I keep thinking of IRC Section R302.2.2--the exception--where a parapet is not required if there are fire-resistant materials applied to the roof decking, or the roof decking is non-combustible, and in both cases there is a minimum class C roofing. Is there a counterpart to this informaion in the IBC? The IBC commentary to Section 705.11 was no help either.
Is protecting the ceiling equivalent?? That would seem to me to be protecting from the inside, but as I asked above, does 705.5 apply to roof/ceilings?
Also, does it matter that the terminology in exception 4 is different than exception 3? Exception 3 says "roofs of...fire-resistance-rated construction," and exception 4 says "roof/ceiling framing elements...shall be of...fire-resistive-rated construction." I took out part of the sentances so you can see the parts I'm focused on.
Section 711 (horizontal assemblies) did not help. I didn't expect to find help in Chapter 15, but looked just in case, and it only covers fire classification as expected. The gypsum manual has assemblies for wood trusses, but they are all just showing ceiling protection, and nothing on the roof.
I also need to address the 1-ft overhang, but one thing at a time!!