Okay I have another gray area: IBC 2009
I have a plan review response on my applied roof material supporting on existing roofing assembly. Loading designed Okay.
however I am getting push a question on allowable materials, and Concealed space of all things.
section 602.2 for non combustible materials - examiner is not allowing FRTW for High-rise. except for meeting 603. <2 story and 20feet above floor (this is for wood roof deck structure).
and They also noted that the pedestal bases cause a concealed space.??
Why is this regulated as a component of a "building element" under 601
it is not the primary frame, bearing or non bearing interior partitions, nor is it floor construction or Roof Construction per the table.
it is outside space - it is not part of the roof assembly, deck or covering. it is above it! it is outside the building envelope.
my argument is - it should be considered furniture or like a finish - then it only needs to meet 1505 for CLASS B min and smoke/flame spread. (but that is a roof covering attached equivalent chart)
also, what is the concealed space issue? it is accessible. it is not part of the return air plenum.
not a fire area, not a sprinkler need or rating issue. air movement can happen between the joints.
What do you think of the argument that this is not a building element of structure but a finish and therefore not regulated?
I have a plan review response on my applied roof material supporting on existing roofing assembly. Loading designed Okay.
however I am getting push a question on allowable materials, and Concealed space of all things.
section 602.2 for non combustible materials - examiner is not allowing FRTW for High-rise. except for meeting 603. <2 story and 20feet above floor (this is for wood roof deck structure).
and They also noted that the pedestal bases cause a concealed space.??
Why is this regulated as a component of a "building element" under 601
it is not the primary frame, bearing or non bearing interior partitions, nor is it floor construction or Roof Construction per the table.
it is outside space - it is not part of the roof assembly, deck or covering. it is above it! it is outside the building envelope.
my argument is - it should be considered furniture or like a finish - then it only needs to meet 1505 for CLASS B min and smoke/flame spread. (but that is a roof covering attached equivalent chart)
also, what is the concealed space issue? it is accessible. it is not part of the return air plenum.
not a fire area, not a sprinkler need or rating issue. air movement can happen between the joints.
What do you think of the argument that this is not a building element of structure but a finish and therefore not regulated?