Hello Members,
The question is: We have a six story building with a penthouse level that has doorway access on to the surrounding unoccupied roof for equipment maintenance- roof top units, satellites, etc.. . We usually keep the threshold of the door up higher than normal for flashing against moisture/drifting snow, etc... In this case the owner has requested that the sill be a minimum 8" above finished roof surface. So I have found the following:
1. IBC 2015 Section 1103.2.9 Equipment Spaces, exempts the access from Chapter 11 requirements.
2. IMC 2015 Section 306.5 Equipment and Appliances on Roofs or Elevation Structures, says ...access shall be provided. Such access shall not require climbing over obstructions greater than 30 inches.
3. OSHA Standard 1910.25(c)(2) states, max riser of 9.5 inches, min. tread depth of 9.5 inches and min width of 22 inches for stairs, with a landing min depth of 30 inches.
Does the IBC 2015 Chapter 10 apply to the roof access? I cannot find an exception. And if so does it take precedence over the OSHA requirements for stair and landing requirements and stepping down from the interior space? Or can you argue that this is governed by IMC and you are not required to have stairs if the threshold is within 30 inches of finished floor / roof?
Thank you in Advance - Steve Miles
The question is: We have a six story building with a penthouse level that has doorway access on to the surrounding unoccupied roof for equipment maintenance- roof top units, satellites, etc.. . We usually keep the threshold of the door up higher than normal for flashing against moisture/drifting snow, etc... In this case the owner has requested that the sill be a minimum 8" above finished roof surface. So I have found the following:
1. IBC 2015 Section 1103.2.9 Equipment Spaces, exempts the access from Chapter 11 requirements.
2. IMC 2015 Section 306.5 Equipment and Appliances on Roofs or Elevation Structures, says ...access shall be provided. Such access shall not require climbing over obstructions greater than 30 inches.
3. OSHA Standard 1910.25(c)(2) states, max riser of 9.5 inches, min. tread depth of 9.5 inches and min width of 22 inches for stairs, with a landing min depth of 30 inches.
Does the IBC 2015 Chapter 10 apply to the roof access? I cannot find an exception. And if so does it take precedence over the OSHA requirements for stair and landing requirements and stepping down from the interior space? Or can you argue that this is governed by IMC and you are not required to have stairs if the threshold is within 30 inches of finished floor / roof?
Thank you in Advance - Steve Miles