• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Run PVC electrical conduit in same trench as schedule 40 PVC for water.

John Ross

Registered User
Joined
Oct 27, 2017
Messages
3
Location
Florida
I live in the Tampa Bay area of Florida.
I need to run two separate schedule 40 conduit. One for portable water, and one for 110 volt for LED landscape lighting. I know electrical must be in gray PVC conduit, and water in schedule 40 white PVC pipe.

My question is, can I run both pipes in the same trench? If so, do they have to be separated and if so by how many inches?

Also, how deep does the trench have to be, and should the water go above or below the electrical conduit?

Thank you in advance for your help.
 
Potable water can not be in PVC....Same trench is fine and usually 18" to 24" for electrical all of my water goes 48" deep as I am not in Florida....
 
PVC must be allowed in Florida as my main water line from the meter to my home is PVC just like everyone else in the community.
 
This from a forum:

PVC is fine for potable water. It is WIDELY used here in southern California to run from the meter at the curb, to the house main shut off ( outside the house ). Codes do not allow it to be used inside a dwelling, at all, but I think the main reason is that it is rated for about maximum 70 PSI at 140 degrees. For 70 degree cold water, the PSI rating will be well in excess of anything your house or line would see.

As far as brittle, it is an issue if exposed to UV light ( sunlight), but otherwise not an issue.
 
# ~ # ~ #

John Ross,

PVC piping is allowed for potable water service to the structure.
Refer to Table 605.3 in the `17 Edition of the Florida Plumbing
Code.

PVC piping IS NOT allowed once inside a structure.......Refer
to Table 605.4 in the `17 Edition of the Florida Plumbing Code.

Yes, you can install the water piping & the electrical conduit
in the same trench.........You must install an electrical warning
tape over the electrical conduit if the trench is not fully encased
in concrete.


# ~ # ~ #
 
# ~ # ~ #
You must install an electrical warning
tape over the electrical conduit if the trench is not fully encased
in concrete.

# ~ # ~ #

I have never seen tape on a residential project. I know it is there in the code but I have never asked for it....my bad.

Plastic pipe strikes me as not appropriate. I just can't be convinced that plastic or rubber like PEX is suitable for my drinking water.
 
Typical-Trench-Detail-Drawing.jpg

https://laneelectric.com/programs-services/typical-trench-detail/

Check with your local Jurisdiction, some allow it, others do not
 
Here in California potable water can be plumbed with CPVC.

2012IPC allows CPVC, but check water pressure requirement of not > than 160 psi.

I see K-copper, PEX and mostly blue crestline at 200 or 250 psi being use here.
 