Greetings to all,
In doing a final walk thru this a.m. for a credit union I inquired about the glazing in a number of office doors. Sure nuff no id to indicate safety glazing. All other glazing in the building is properly etched. In reading 2406.3 in the 09 IBC it states that all safety glazing shall be etched etc., or otherwise exception #1 can be applied. It reads thusly.
Exceptions:
1. For other than tempered glass, manufacturer’s designations
are not required, provided the building official
approves the use of a certificate, affidavit or other evidence
confirming compliance with this code.
What would be acceptable in your jurisdiction? Previously when I've run into this (rarely) the glass would be changed appropriately.
thanks to all
BS
In doing a final walk thru this a.m. for a credit union I inquired about the glazing in a number of office doors. Sure nuff no id to indicate safety glazing. All other glazing in the building is properly etched. In reading 2406.3 in the 09 IBC it states that all safety glazing shall be etched etc., or otherwise exception #1 can be applied. It reads thusly.