• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Schedule 20 vs. Schedule 40 PVC Pipe

globe trekker

REGISTERED
Joined
Oct 19, 2009
Messages
1,739
Greetings to all!

I have plumbing contractor who has installed Schedule 20 pvc piping as the water

service piping to a Residence. The GC is claiming that a minimum of Schedule 40

pvc is required. In looking at Table P2904.4, in the 2006 Edition of the IRC, there

are various ASTM standards listed as acceptable piping to use as water service

piping.

QUESTION # 1: Do the ASTM standards actually specify Schedule 40 pvc piping be

used as water service piping, or will Schedule 20 pvc piping be acceptable?

FWIW, Section P2904.4 states that a minimum of 160 psi piping must be used as

water service piping.

I am looking for chapter & verse; either from the IRC, or ASTM or other, so that I

can print out and show to said contractors. Thanks ya`ll! :)

.
 
You could call customer service at Charlotte Pipe and ask if schedule 20 meets the criteria or better yet have the contractor show that it meets minimum 160 psi.
 
I do not believe PVC is allowed for potable water pipe.....at least not inside here..........but here are the standards for service pipe......

Polyvinyl chloride (PVC) plastic pipe

ASTM D 1785; ASTM D 2241; ASTM D 2672; CSA B137.3
 
Last edited by a moderator:
"rleibowitz",

I cannot ask the (plbg.) contractor anything, as I am not dealing with them directly, but

thank you for your input!

"steveray",

PVC pipe is approved as water service pipe (i.e. - piping to the structure), but not as water

distribution piping (i.e. - piping inside the structure), and ..thank you for your input!

Contacting a pvc pipe manufacturer may be my best option, if no information is provided

on here.

.
 
globe trekker said:
Greetings to all!I have plumbing contractor who has installed Schedule 20 pvc piping as the water

service piping to a Residence. The GC is claiming that a minimum of Schedule 40

pvc is required. In looking at Table P2904.4, in the 2006 Edition of the IRC, there

are various ASTM standards listed as acceptable piping to use as water service

piping.

QUESTION # 1: Do the ASTM standards actually specify Schedule 40 pvc piping be

used as water service piping, or will Schedule 20 pvc piping be acceptable?

FWIW, Section P2904.4 states that a minimum of 160 psi piping must be used as

water service piping.

I am looking for chapter & verse; either from the IRC, or ASTM or other, so that I

can print out and show to said contractors. Thanks ya`ll! :)

.
Do you have any other information on the type of piping being used.

I do not believe there is any schedule pressure rated PVC less than 40.
 
Back
Top