Re: Sealing The Sole Plates
If it is a conditioned crawlspace, the envelope extends down to the slab insulation, and any joint from the roof on down would need to be "sealed", my question would be what is the definition of "sealed" is it gasketed like "sill-seal" foam, or hanging the sheathing down to cover the "gap" between foundation and sole plate? If the sheathing doesn't cut it, wouldn't you also have to seal ALL horizontal plate connections? :?:
OK...Read the section...(I'm still on '03)
N1102.4.1 Building thermal envelope.
The building thermal envelope shall be durably sealed to limit infiltration. The sealing methods between dissimilar materials shall allow for differential expansion and contraction. The following shall be caulked, gasketed, weatherstripped or otherwise sealed with an air barrier material, suitable film or solid material.
1. All joints, seams and penetrations.
2. Site-built windows, doors and skylights.
3. Openings between window and door assemblies and their respective jambs and framing.
4. Utility penetrations.
5. Dropped ceilings or chases adjacent to the thermal envelope.
6. Knee walls.
7. Walls and ceilings separating the garage from conditioned spaces.
8. Behind tubs and showers on exterior walls.
9. Common walls between dwelling units.
10. Other sources of infiltration.
Seems like sheathing is a solid material and covers the joint! IF hung down over the sole plate. Being DISSIMILAR materials (the plate and foundation wall) I think it would need to be sealed in some way! JMHO