conarb
GT:
Our 2007 CBC (2006 IBC) does answer your original question:
It seems to me that somewhere back in ancient history the 32" clear opening was 34", a standard single 3' door yields a clear opening of 35" when opened against the wall, but only 33" when opened against a 90° wall (assuming standard butt hinges).1008.1.1 Size of doors. The minimum width of each door opening shall be sufficient for the occupant load thereof and shall provide a clear width of not less than 32 inches (813 mm). Clear openings of doorways with swinging doors shall be measured between the face of the door and the stop, with the door open 90 degrees (1.57 rad). Where this section requires a minimum clear width of 32 inches (813 mm) and a door opening includes two door leaves without a mullion, one leaf shall provide a clear opening width of 32 inches (813 mm). The maximum width of a swinging door leaf shall be 48 inches (1219 mm) nominal. Means of egress doors in a Group 1-2 occupancy used for the movement of beds and litter patients shall provide a clear width not less than 44 inches (1118 mm). The height of doors shall not be less than 80 inches (2032 mm).