• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Section R403.1.6, 2006 IRC

globe trekker

REGISTERED
Joined
Oct 19, 2009
Messages
1,739
Greetings to all!

Is there a standard, or code section to reference when considering the "required" 1/2"

anchor bolts listed in Section R403.1.6, 2006 IRC (i.e. - shear values, pull out

capacities, other technical info., etc.). Possibly an ASTM, or ANSI, or ACI-318

standard?

Rather than telling someone that a 1/2" diameter anchor bolt is required, is there a

specific standard that I can refer to for technical guidance?

Thanks ya`ll! :)

.
 
I will suggest that the IRC has not addressed this issue and thus the building official is not able to require something not in the code. We need to realize that the IRC in its effort to make something easier to use has lost much of the rigor that exists in the IBC.

I do not see how you can get to ACI 318 if the applicant is staying within the normal provisions of hte IRC.

ICC AC are not a part of the code and thus cannot be enforced unless the applicant whishes to deviate from the code.
 
Mark K said:
I do not see how you can get to ACI 318 if the applicant is staying within the normal provisions of hte IRC.

ICC AC are not a part of the code and thus cannot be enforced unless the applicant whishes to deviate from the code.
IRC CHAPTER 44

REFERENCED STANDARDS

ACI 318-08 Building Code Requirements for Structural Concrete ..................... R301.2.2.2.4, R301.2.2.3.4, R402.2, R404.1.2,

Table 404.1.2(5), Table R404.1.2(6), Table R404.1.2(7),

Table R404.1.2(8), Table R404.1.2(9), R404.1.2.1,

R404.1.2.3, R404.1.2.4, R404.1.4.2, R404.6.1, R611.1, R611.1.1,

R611.1.2, R611.2, R611.5.1, R611.8.2, R611.9.2, R611.9.3
 
The fact that a standard is referenced in the IRC does not mean you can require compliance in all cases. You need to look at where that standard is referenced and what it says about the standard. Reference R104.4 where it talks about the prescribed extent of the reference standard.
 
I have to agree with Mark K on this one. None of the references to ACI 318 are specific to the anchor bolts required by R403.1.6
 
Thank you all for your input!

..and a compliant answer to the inquiring applicants is?

"Sorry, not addressed in the IRC! You will need to hire a structural engineer to prescribe

something."

As far as the IRC is concerned, any type of 1/2" diameter bolt is compliant?

Also, "Papio Bldg. Dept.", ..good to see you back in The Game! :D

.

.
 
If the homeowner is asking the question you can state that the IRC is silent on this issue but the IBC would accept anchor bolts that complied with ASTM A307, ASTM A36, or ASTM F1554.
 
Back
Top