NFPA will tell you how to install and maintain the door, see below. The building code will tell you when the door is required, the hour fire rating, etc. See below 5.2.3.2 if the stuff is missing.
From NFPA 80, 2010 Ed.
5.2.3 Functional Testing.
5.2.3.1 Functional testing of fire door and window assemblies shall be performed by individuals with knowledge and understanding of the operating components of the type of door being subject to testing.
5.2.3.2 Before testing, a visual inspection shall be performed to identify any damaged or missing parts that can create a hazard during testing or affect operation or resetting.
5.2.4 Swinging Doors with Builders Hardware or Fire Door
Hardware.
5.2.4.1 Fire door assemblies shall be visually inspected from
both sides to assess the overall condition of door assembly.
5.2.4.2 As a minimum, the following items shall be verified:
(1) No open holes or breaks exist in surfaces of either the
door or frame.
(2) Glazing, vision light frames, and glazing beads are intact
and securely fastened in place, if so equipped.
(3) The door, frame, hinges, hardware, and noncombustible
threshold are secured, aligned, and in working order
with no visible signs of damage.
(4) No parts are missing or broken.
(5) Door clearances do not exceed clearances listed in 4.8.4
and 6.3.1.7.
(6) The self-closing device is operational; that is, the active
door completely closes when operated from the full
open position.
(7) If a coordinator is installed, the inactive leaf closes before
the active leaf.
(8) Latching hardware operates and secures the door when
it is in the closed position.
(9) Auxiliary hardware items that interfere or prohibit operation
are not installed on the door or frame.
(10) No field modifications to the door assembly have been
performed that void the label.
(11) Gasketing and edge seals, where required, are inspected
to verify their presence and integrity.