Mr. Inspector
SAWHORSE
A self-contained hot tub in a commercial building has a suspended ceiling with 2x4 light fixtures over it. There is also wiring above the suspended ceiling. the ceiling is within 7' above the hot tub, don't know what the actual distance is.
1. I already told them that the needed to bond the rails of the suspended ceiling to the hot tub. Do you think every rail needs bonding or just one?
2. I don't think i need to enforce 680.9 for overhead conductors in the ceiling but it would be easy for someone to move the ceiling panels if they were standing on the side or the step to the hot tub. I'm I wrong?
3. I think the area above the suspended ceiling might be part of the corrosive environment and will need to be in wiring methods per NEC 680.14. I'm I wrong?
4. I don't know what they will do about the lighting fixtures in the suspended ceiling yet. But even if they move them 5' away from the hot tub i am concerned that the metal light fixtures will be against the metal rails of the suspended ceiling that is above the hot tub. Any solutions that you can think of for this?
5. Do the requirements for stairways, especially the ceiling height in the IBC for the stairs outside of the hot tub need to be complied too?
6. Do the stirs in and/or outside of the hot tub need to comply with the dimensions in ISPSC 306.3 and a handrail 306.4.
7. Is a clock really required per ISPSC 509.4?
1. I already told them that the needed to bond the rails of the suspended ceiling to the hot tub. Do you think every rail needs bonding or just one?
2. I don't think i need to enforce 680.9 for overhead conductors in the ceiling but it would be easy for someone to move the ceiling panels if they were standing on the side or the step to the hot tub. I'm I wrong?
3. I think the area above the suspended ceiling might be part of the corrosive environment and will need to be in wiring methods per NEC 680.14. I'm I wrong?
4. I don't know what they will do about the lighting fixtures in the suspended ceiling yet. But even if they move them 5' away from the hot tub i am concerned that the metal light fixtures will be against the metal rails of the suspended ceiling that is above the hot tub. Any solutions that you can think of for this?
5. Do the requirements for stairways, especially the ceiling height in the IBC for the stairs outside of the hot tub need to be complied too?
6. Do the stirs in and/or outside of the hot tub need to comply with the dimensions in ISPSC 306.3 and a handrail 306.4.
7. Is a clock really required per ISPSC 509.4?