• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

self-service storage building distance

sunyaer

Registered User
Joined
Apr 21, 2022
Messages
338
Location
Toronto
This is a quiz question for Ontario Building Code. Why is the answer d)? Should the answer be b)? (required distance between buildings shall not be less than 9 m, while actually distance is only 7.5 m)

1693784070159.png
 
The issue that this question is trying to get to is that single storey self-storage buildings are treated differently than multiple storey ones. 3.10.3 is for multiple storey buildings and 3.10.4. is single storey. When we are working with single storey buildings, we can group the together to get some relaxations on spatial separation. This same allowance is not permitted for multiple storey buildings.

Technically, the answer is (d) because the question is unclear about if there are openings is the exposing building face, so we don't know if (b) is true or not.
 
The issue that this question is trying to get to is that single storey self-storage buildings are treated differently than multiple storey ones. 3.10.3 is for multiple storey buildings and 3.10.4. is single storey. When we are working with single storey buildings, we can group the together to get some relaxations on spatial separation. This same allowance is not permitted for multiple storey buildings.

Technically, the answer is (d) because the question is unclear about if there are openings is the exposing building face, so we don't know if (b) is true or not.
Most self-storage buildings have garage doors in 'em - ie at least 64 ft2 or 5.9m2.

It's well worth noting that Part 3 self-storage buildings allow for a closer spacing than Part 9 buildings....but that Part 3 self-storage units require bathrooms. An odd requirement, but ... <shrug>
 
Most self-storage buildings have garage doors in 'em - ie at least 64 ft2 or 5.9m2.
Where these are multiple storey buildings, they may not have any openings to the exterior or could be located so the exposing building faces do not have any openings in them (they may be end-adjacent, not side-by-side).

Still not a great question. They should be focused on code understanding/interpretation. Not reading comprehension.
 
The issue that this question is trying to get to is that single storey self-storage buildings are treated differently than multiple storey ones. 3.10.3 is for multiple storey buildings and 3.10.4. is single storey. When we are working with single storey buildings, we can group the together to get some relaxations on spatial separation. This same allowance is not permitted for multiple storey buildings.

Technically, the answer is (d) because the question is unclear about if there are openings is the exposing building face, so we don't know if (b) is true or not.
-------------------------------------------------------------------------------------------------
3.10.3.2. Spatial Separations

(1) Except as provided in Sentence (2), the requirements in Subsection 3.2.3. shall apply.
(2) The distance between buildings shall be not less than 9 m.
--------------------------------------------------------------------------------------------------
The distance between the two buildings is 7.5 m, 3.10.3.2.(2) is not satisfied (7.5 m is less than 9 m), why b) is not the answer)? (compliance with the building code has not been achieved)
 
-------------------------------------------------------------------------------------------------
3.10.3.2. Spatial Separations

(1) Except as provided in Sentence (2), the requirements in Subsection 3.2.3. shall apply.
(2) The distance between buildings shall be not less than 9 m.
--------------------------------------------------------------------------------------------------
The distance between the two buildings is 7.5 m, 3.10.3.2.(2) is not satisfied (7.5 m is less than 9 m), why b) is not the answer)? (compliance with the building code has not been achieved)
The wording of the question is that the buildings already exist. In that case, we can't relocate the buildings, but we can control the unprotected openings by reducing or re-orienting them.

Both (b) and (d) might be equally acceptable answers.

Another terrible question. If you have not complained about this test quiz, please do so.
 
...

Another terrible question. If you have not complained about this test quiz, please do so.
I only analyzed 40 questions from a mock test quiz (total 80 questions for one test), there have been so many questionable questions. I couldn't imagine how the package could have been put up for sale.
 