I am dealing with a new self-storage facility.
Under the IBC 2015, ICC/ANSI A117.1-2009
There are 6 self-storage buildings on the site, each building provides entrances doors to corridors that serve all of the storage units, and they are all interior units
As per IBC 2015: 1108.3.1 all of the required accessible storage units of each type are permitted to be located in a single building on the site. That is indeed the case on this project.
In every building on the site, the height of the vision panels in all of the egress/ entrance doors exceed 43” to the bottom of the glazing; there are no side lights
Would all of the buildings be required to provide compliant door vision panels, or just the one building where the accessible storage units are located?