1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Separation of water and sewer

Discussion in 'Plumbing Codes' started by Joe Engel, Dec 7, 2018.

  1. Joe Engel

    Joe Engel Member

    Joined:
    Jun 16, 2011
    Messages:
    36
    Likes Received:
    10
    Running discussion with plumber,
    2012 IPC, 603.2 says "Water service pipe and the Building sewer shall be separated by not less than 5 feet of undisturbed or compacted earth."

    But 603.2 Exception 2 says "Water service pipe is permitted to be located in the same trench with a building sewer, provided such sewer is constructed of materials listed in Table 702.2."

    Table 702.2 UNDERGROUND BUILDING DRAINAGE AND VENT PIPE gives reference to all materials allowed to be used within the building footprint or building drain system.

    In my experience, we always separated the two outside the slab either by 5 foot or on a shelf in the same trench, 18" above the building sewer. Here is the deal... If a building drain meets code and you use the same material as in the slab outside the slab, then you should be able to run the water service in the same trench (his argument)... Opinions?
     
  2. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    124
    Likes Received:
    37
    Correct. Don't we commonly lay building drain piping and water distribution piping in the same trench under a slab on grade foundation? If it is not in the same trench under a slab on grade foundation, we certainly don't pay much attention to separation between the two.
     
  3. jeffc

    jeffc Bronze Member

    Joined:
    Oct 23, 2009
    Messages:
    79
    Likes Received:
    6
    The 2015 Uniform Plumbing Code, Section 720, requires a separation only if the sewer pipe is not approved for use inside of a building. Not the IPC but close.
     
  4. Master Pipe

    Master Pipe Registered User

    Joined:
    Dec 5, 2018
    Messages:
    2
    Likes Received:
    0
    You can take different decision after situation.
     