A proposed type V bank, 2500 square foot, engineer untreated wood truss, on wood frame and portal steel frame walls, with GWB interior walls is being proposed and under plan review.
Question: Using the 2009 IBC and sections bellow, will sheet rock be required on the bottom cord of the roof trusses above the ACT grid and ceiling?
Question does anyone have the 2009 commentary for his section that could share?
717.1 General. Fireblocking and draftstopping shall be installed in combustible concealed locations in accordance with this section. Fireblocking shall comply with Section 717.2. Draftstopping in floor/ceiling spaces and attic spaces shall comply with Sections 717.3 and 717.4, respectively. The permitted use of combustible materials in concealed spaces of buildings of Type I or II construction shall be limited to the applications indicated in Section 717.5.
717.2 Fireblocking. In combustible construction, fireblocking shall be installed to cut off concealed draft openings (both vertical and horizontal) and shall form an effective barrier between floors, between a top story and a roof or attic space. Fireblocking shall be installed in the locations specified in Sections 717.2.2 through 717.2.7.
As always thanks for the help in the confusion.
Question: Using the 2009 IBC and sections bellow, will sheet rock be required on the bottom cord of the roof trusses above the ACT grid and ceiling?
Question does anyone have the 2009 commentary for his section that could share?
717.1 General. Fireblocking and draftstopping shall be installed in combustible concealed locations in accordance with this section. Fireblocking shall comply with Section 717.2. Draftstopping in floor/ceiling spaces and attic spaces shall comply with Sections 717.3 and 717.4, respectively. The permitted use of combustible materials in concealed spaces of buildings of Type I or II construction shall be limited to the applications indicated in Section 717.5.
717.2 Fireblocking. In combustible construction, fireblocking shall be installed to cut off concealed draft openings (both vertical and horizontal) and shall form an effective barrier between floors, between a top story and a roof or attic space. Fireblocking shall be installed in the locations specified in Sections 717.2.2 through 717.2.7.
As always thanks for the help in the confusion.
Last edited by a moderator: