1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

service bonding 2011 NEC

Discussion in 'Electrical Codes' started by BSSTG, Jul 25, 2011.

  1. BSSTG

    BSSTG Gold Member

    Joined:
    Nov 30, 2009
    Messages:
    729
    Likes Received:
    11
    Greetings all,

    Well I'm confused with 250.92 (B).

    My question is this. Are grounding bushings or grounding locknuts required on service conduits under all circumstances in lieu of standard locknuts now? Or are the gounding bushings and locknuts only required around concentric knockouts, reducing washers and so forth? It looks to me as if standard locknuts are not allowed for bonding of service equipment under any circumstance but I'm not sure if I'm reading this right

    thanks

    BS
     
  2. Bryan Holland

    Bryan Holland Silver Member

    Joined:
    Oct 18, 2009
    Messages:
    241
    Likes Received:
    1
    Here's how I understand it.

    All the stuff in section 250.92(A)(1)&(2) are required to be bonded together. The method for bonding these items together can be any of the (4) methods indicated in section 250.92(B). Standard locknuts or bushings used by themselves can not be used to satisfy these requirements. In addition, bonding jumpers are required where the potential for an impaired connection is present due to inadequate connection beetwen an enclosure and a raceay fitting.

    The moral of the story is this. When in doubt, bond.
     
  3. raider1

    raider1 Silver Member

    Joined:
    Nov 3, 2009
    Messages:
    479
    Likes Received:
    0
    This change was just a re-wording of the requirements already contained in 250.92.

    Standard locknut can't be used for bonding on the line side of the service and bonding bushings or locknuts are required to bond metallic raceways on the line side of the service even if concentric, eccentric or reducing washers are encountered.

    Chris
     
  4. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    Chris: By any chance do you have a photo of a proper install? This is a great question and I agree with Bryan on when in doubt!
     
  5. TimNY

    TimNY Platinum Member

    Joined:
    Jan 13, 2010
    Messages:
    1,135
    Likes Received:
    5
    Also, if we could have the section.. for those of use who don't have the 2011 NEC yet :) thanks!
     
  6. raider1

    raider1 Silver Member

    Joined:
    Nov 3, 2009
    Messages:
    479
    Likes Received:
    0
    Check out 250.92(B).

    Chris
     
  7. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
  8. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    Francis: Good enough! This is a section often missed. Sometimes a picture goes along ways to allowing ones understanding od an issue. It also can stimilate more discussion on a subject that needs clear understanding.
     
  9. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,441
    Likes Received:
    156
    This is how it reads.

     
  10. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    So here is the question. If the service disconnect is a regular panelboard and the metal raceway entering the service panel comes through a concentric knockout, needs to be bonded with a bond bushing or bonding locknut, does that mean that all branch circuits and feeders that leave that same service panelboard must have the same bond bushings or bonding locknut if they are connected to a concentric KO with metal raceway?
    Food for thought..... :)
     
  11. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,095
    Likes Received:
    244
    2014 NEC Handbook says just the line side.

    upload_2019-9-17_14-18-45.png
     
  12. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    Is there anyone out there that requires this at service panels that have EMT or other metallic conduit leaving on branch circuits and feeders?

    I do not for the record.
     