thanks you, I was looking unhder service equipment conductors : )north star said:Heaven,
With regard to your requested 2008 NEC article, look at Article 334.12(A)(2) for NM conductors.
This question is coming up more and more!
For commercial installations SER cable run as interior wiring in accordance with 338.10(B)(4)(a) must be concealed within walls, floors and ceilings that provide a thermal barrier of at least 15 minutes. (See 334.10(3).)Heaven said:Sorry, I posted under teh wrong section, this is in a commercial building, and from your wording it sounds like it must be protected, are you able to give me a section NEC2008 where I can read about that? thanks if so,
Thanks.north star said:Chris,
You da man!