Since no one else that participates in this forum ever does any electrical inspections other than ICE and I
Jeeze, you sound like my boss. "Am I the only one who does any inspections around here?"
Just kidding.
I believe the code references you are looking for are:
#1) 250.24(B)
#2) 300.4(G) and 352.46
#3) 110.3(B)
The absence of a grounding electrode conductor should be addressed.
In case you haven't noticed, nobody gets excited about looking up code sections.
Does the field punched KO above the main lugs have sealing provisions to prevent water infiltration?