klarenbeek
REGISTERED
With the way it's indented I agree and stand corrected.That exception applies only to condition #3, which is only applicable to non-combustible floor-ceiling assemblies.
That being said there's still no need for shafts or dampers if none of the assemblies are rated. Based on the IBC definition of "floor", the attic is very clearly considered part of the second story:
STORY. That portion of a building included between the upper surface of a floor and the upper surface of the floor or roof next above (see "Basement," "Building height," "Grade plane" and "Mezzanine"). A story is measured as the vertical distance from top to top of two successive tiers of beams or finished floor surfaces and, for the topmost story, from the top of the floor finish to the top of the ceiling joists or, where there is not a ceiling, to the top of the roof rafters.
The attic is by definition part of the second story so no more than two stories are connected.