A 4,000 x 400 warehouse has 82 exit doors. Only 2 accessible exits are required. One normal level accessible exit on the north east corner of the building and an exterior area of refuge on the south west corner of the building with an landing for 2 wheelchairs and a short exterior accessible stairway. I usually tell the contractor to have the required accessible exit directional signs that are required at the non accessible exits to have directions to the closest accessible exit but the code does not require this. Part of 2009 IBC section 1007.6 says "Every required area of refuge shall be from the space it serves by an accessible means of egress. The maximum travel distance from any accessible space to an area of refuge shall not exceed the travel distance permitted for the occupancy in accordance with Section 1016.1".
1. The area area of refuge on the landing of the exterior stairway has space for 2 wheelchairs. Warehouses has a 500 sq ft gross floor area per occupant. I guess that means that the area of refuge serves a space of 1,000 sq ft. So does this mean I should only have the accessible exit directional signs within this 1,000 sq. ft area immediately next to the area of refuge have directions to the area of refuge?
2. The maximum travel distance for S-2 with sprinklers is 400'. Does this mean according to 1016.1 that only the accessible exit directional signs at exits within 400' of the area of refuge can have directions to the area of refuge?
3. Would it be better just to have all the accessible direction signs to have directions to the normal level accessible exit in the north east corner of the building which could more than 4,000 ft away from some non accessible exits?
1. The area area of refuge on the landing of the exterior stairway has space for 2 wheelchairs. Warehouses has a 500 sq ft gross floor area per occupant. I guess that means that the area of refuge serves a space of 1,000 sq ft. So does this mean I should only have the accessible exit directional signs within this 1,000 sq. ft area immediately next to the area of refuge have directions to the area of refuge?
2. The maximum travel distance for S-2 with sprinklers is 400'. Does this mean according to 1016.1 that only the accessible exit directional signs at exits within 400' of the area of refuge can have directions to the area of refuge?
3. Would it be better just to have all the accessible direction signs to have directions to the normal level accessible exit in the north east corner of the building which could more than 4,000 ft away from some non accessible exits?