bellbutler
I'm looking for any IBC code commentary or tech bulletins that might provide some additional clarification on this. Single exits have come up a lot on the forums, and I've read through the past posts; which all described buildings a good bit larger than what we are working with, so were not really relevant. We are on 2015 IBC.
We have a 1600sf freestanding A2 building with a small roof deck ~700sf open to the sky and bounded by 42" guardrails accessed only via an exterior stair that meets the IBC definition and 1027 requirements for 'Exterior Exit Stairway.' We intentionally sized the roof deck to be less than 49 occupants and less than 75' travel distance from most remote point to bottom of the stair which discharges at grade and the public way. Our position is that we meet the criteria established by '1006.3.2 Single exits (under 1006.3 Egress from stories and occupied roofs)' by the second condition, code excerpted below.
The AHJ is challenging this as they interpret 'discharge directly' to mean an exit door that opens directly to the outside on the ground floor only. We've provided the code documentation that indicates our Exterior Exit Stairway meets 1027 requirements and per IBC definition of 'exit' constitutes an exit. Our position is that you enter the 'Exit' (i.e. the stair) at the roof level and discharge from the 'Exit' at grade and thus are inline with code requirements.
They've offerered to interpret the roof deck as a mezzanine and indicated that would make it compliant, however I feel uneasy about formally documenting an occupied roof as a mezzanine as in my opinion it clearly does not meet the code definition of a mezzanine as it is not open to any interior space at all. They have a formal appeal process which we are considering pursuing as the Owner would prefer not to have 2 stairs given the small size of the roof deck.
Relevant definitions:
(my opinon is code should revise 'common path' to 'exit access travel distance' as by nature of a single exit there is no common path, but that's neither here nor there)
1006.3.2 Single Exits
A single exit or access to a single exit shall be permitted from any story or occupied roof where one of the following conditions exists:
- The occupant load, number of dwelling units and common path of egress travel distance does not exceed the values in Table 1006.3.2(1) or 1006.3.2(2).
- Rooms, areas and spaces complying with Section 1006.2.1 with exits that discharge directly to the exterior at the level of exit discharge, are permitted to have one exit or access to a single exit.
COMMON PATH OF EGRESS TRAVEL. That portion of the exit access travel distance measured from the most remote point within a story to that point where the occupants have separate and distinct access to two exits or exit access doorways.
EXIT. That portion of a means of egress system between the exit access and the exit discharge or public way. Exit components include exterior exit doors at the level of exit discharge, interior exit stairways and ramps, exit passageways, exterior exit stairways and ramps and horizontal exits.
EXIT DISCHARGE. That portion of a means of egress system between the termination of an exit and a public way.
EXIT DISCHARGE, LEVEL OF. The story at the point at which an exit terminates and an exit discharge begins.
EXTERIOR EXIT STAIRWAY. An exit component that serves to meet one or more means of egress design requirements, such as required number of exits or exit access travel distance, and is open to yards, courts or public ways.