eyan50495
Hi All
So the Building Dept has reviewed our Life Safety drawings and determined that we need a second means of egress from a basement.
This is a Mercantile Occ. with a floor plate of 10,000 SF. The basement in question has 2 stairs, picture a box with one on the midpoint of the left side and one on the bottom left corner (both 1 hour fire rated). Due to a commercial kitchen located on the lower portion of this box, the 2nd stair on the bottom left only has a single corridor going towards it. In theory, you cannot access that 2nd stair without first passing the 1st / Middle Stair and going down a corridor, past the kitchen to access it.
The DOB would like us to created a rated corridor between both stairs and says that 2 means of egress are required regardless of the occupant load.
Although it wouldn't be the end of the world to create a rated corridor, it would create issues with the function of the kitchen and other staff (they need traffic doors).
Based on my understanding, Chapter 10 of IBC 2015 of NYS has 2 areas about Number of Exits / Exit Access. I believe 1006.3.1 Egress Based on Occupant Load is more relevant.
Our occupant load is 35 and the Common Path of Travel does not exceed 75'.
It states "Each story and occupied roof shall have the minimum number of independent exits, or access to exits, as specified in Table 1006.3.1. A single exit or access to a single exit shall be permitted in accordance with Section 1006.3.2."
Table 1006.3.1 states that the Min. # of Exits or Access to Exits Per Story for 1-500 occ. is 2.
Table 1006.3.2 Single Exits states:
A single exit or access to a single exit shall be permitted from any story or occupied roof where one of the following conditions exists:
Going to Table 1006.3.2(2) Stories with 1 Exit or Access to 1 Exit for Other Occ., it states that:
The First story above or below grade plane with an M Occ. must have no more than 49 Occ./Story and a Max. CPT 75'.
We meet both? Am I missing something?
- The occupant load, number of dwelling units and common path of egress travel distance does not exceed the values in Table 1006.3.2(1) or 1006.3.2(2).