Could you elaborate on this? 1021.1 (5) seems to allow any space that complies with Section 1015.1 a single exit. Note that this is indicating that a single exit, not an exit access doorway, is permitted. No limitation is put on the size of this space (other than CPOT and travel distance). What difference does it make whether the space takes up the entire story or not?RLGA said:North Star nailed it. I get so many clients thinking that Table 1015.1 allows them one exit on a story...I have to point out to them it is for "Spaces" only, not stories, and then direct them to Section 1021.
When I read 1021.1 (5) it says only that the the "exits...discharge directly to the exterior at the level of exit discharge" which I took to imply that the spaces might not be on the level of exit discharge. In other words, a stairway that is an exit enclosure may connect the space to the exterior at the level of exit discharge.RLGA said:1021.1 (5) does apply if the space opens directly to the exterior and on the level of exit discharge (typically ground level). But it does not apply when the space is on the second or higher story.
Not correctyou need to comply with the entire Section 1015.1 including CPOT and travel distance, so it is in a sense more restrictive than 1021.2.
I agree because the travel distance ends when you leave the exit access and enter the protected exit.a stairway that is an exit enclosure may connect the space to the exterior at the level of exit discharge.