• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Site built walk in cooler?

rktect 1

Gold Member
Joined
Oct 20, 2009
Messages
1,115
Location
Illinois
I've never encountered this before. An old small existing restaurant has a walk in cooler. They want to remove that one and rebuild a slightly smaller one. 2x4 studs with cavity filled with two layers R7.5 insulation and an air space. then water resistant drywall and then stainless steel panels. Reusing cooling equipment.

Seems like a barrier would be needed if nothing else. Energy code?

Any thoughts?
 
Last edited by a moderator:
2x4 wood studs actually are R-5 or so. They would be better off with a 7" staggered stud wall with R-13 between each set of studs. A vapor barrier should go on the outside, since the vapor drive is from warmer to cooler.
 
R-5 translates to U=0.2 (U = 1/(sum of R values)), which means 2x4s block 80% of heat transfer. Metal studs block almost no heat transfer.
 
Paul Sweet said:
R-5 translates to U=0.2 (U = 1/(sum of R values)), which means 2x4s block 80% of heat transfer. Metal studs block almost no heat transfer.
3.5" X 1.25.------- r-value = 4.375 or a 0.2200 U value

But there is more to it than that

Calculations537x276.png
 
Last edited by a moderator:
Without knowing more information, I cannot say if the energy code is needed or not. If the cooler is part of the building's thermal envelope, then I would require it to comply with the energy code for insulation values. If the cooler is inside the thermal envelope, then I would say the energy code is silent in the matter as this is basically a piece of refrigeration equipment (unless the 2012 code now addresses coolers.)

As far as studs having little to no insulation values, it all depends on your point of view. Compared to the typical R-11 to R-15 fiberglass insulation fit between studs, 2x4 wood studs are inferior to resisting heat transfer. But compared to metal studs, are wood studs are superior for resisting heat transfer.

Assuming:

1) 2x4 wood studs at 16" centers

2) 15 mph wind on one side of the wall (because the original post does not indicate if this cooler is inside the building or not and there is not much difference in the R-value between 7.5 mph summer time wind and 15 mph winter time wind)

3) still air inside the cooler (assuming steady state once the fans shut off, doors are closed, and the air stops moving)

4) two layers of R 7.5 batt insulation can be fit between the studs without being compressed

5) two bottom plates & one top plate (25% wood and 75% insulation in contact with the gyp)

6) 1" air gap + other assumptions to determine an R-value for air

7) 1/2" gyp

8) no siding

9) no exterior substrate

10) no thermal resistance for SS panels

Then I calculate the overall R-value, using parallel flow and isothermal plane methods from Ashrae, to be around 12.3 and 11.5, respectively.

Switch out the steel for wood, make more assumptions about the steel thickness, flange size, and stud depth (3-1/2", 3-5/8", or 4") and the overall R-value drops to 5.7 and 2.7.
 