NY Residential Code Table E3503.1 footnote d states in part, "Where the sole grounding electrode system is the footing steel as covered in Section E3508.1.2, the grounding electrode conductor shall not be required to be larger than 4 AWG copper conductor"
Situation here is 300A service, two sets of 2/0.
Regarding footnote d, the CEE is not the sole system for this residence, as a metal underground water pipe will also be bonded and the local POCO requires rod electrodes. Therefore #2 Cu required per E3508.1.2.
However, NEC 2008 250.66(B) states that the portion of the GEC that is solely connected to the CEE need only be #4. So if individual GECs were run per 250.64(D)(2), the conductor to the CEE would only need to be #4.
I'm assuming it's just poor wording in the NY Code (and probably IRC)?
Also, electrician states he is running #4 to the metal underground water pipe; I see no exception allowing anything less that the #2 required by the tables.
Not an electrical inspector... just the guy who signs the C.O.'s and tries to keep everybody compliant.
Tim
NY Residential Code Table E3503.1 footnote d states in part, "Where the sole grounding electrode system is the footing steel as covered in Section E3508.1.2, the grounding electrode conductor shall not be required to be larger than 4 AWG copper conductor"
Situation here is 300A service, two sets of 2/0.
Regarding footnote d, the CEE is not the sole system for this residence, as a metal underground water pipe will also be bonded and the local POCO requires rod electrodes. Therefore #2 Cu required per E3508.1.2.
However, NEC 2008 250.66(B) states that the portion of the GEC that is solely connected to the CEE need only be #4. So if individual GECs were run per 250.64(D)(2), the conductor to the CEE would only need to be #4.
I'm assuming it's just poor wording in the NY Code (and probably IRC)?
Also, electrician states he is running #4 to the metal underground water pipe; I see no exception allowing anything less that the #2 required by the tables.
Not an electrical inspector... just the guy who signs the C.O.'s and tries to keep everybody compliant.