IRC covers unattached garages. R403.1.4.1
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
IRC covers unattached garages. R403.1.4.1
Under 600 sq ftWhere is the "the exception for floating slab foundations is only for accessory structures" over 600 sq ft? That's all I'm asking for.
I guess it will take posting R403.1.4.1 three times for you to actually read it.I'm not debating your points red-eye, but take my two 600+ sf examples and make them both 500 sf accessory buildings to my main house, heat both, etc., store cars in one and let a relative live - sleeping and bathroom - in the other. And I'll support plumbing etc. off the walls which are on a frost protected foundation.
I am just struggling where this floating slab subject to frost heaves is permitted, besides accessory structures under 600 or 400 sf, or more specifically in garages larger than 600, heated or not, with plumbing or not. Maybe it's in IBC. Haven't looked there yet. I've spent my life in 4.10 and 10.30 (I think .30 in 2021) so IRC is new to me. I used CABOs O&TFD last time I built residential.
Dude, read the exceptions.In your referenced section do you refer to:
"R403.1.4.1 Frost Protection
Except where otherwise protected from frost, foundation walls, piers and other permanent supports of buildings and structures shall be protected from frost by one or more of the following methods:.."
because a s.o.g. is not "a permanent support of a building or structure"? And this would apply to accessory structures as well as living space? It certainly is not the 600 sf accessory space exception below this.
I'm also not seeing where sleeping in an accessory structure is prohibited by the IEC. Isn't a detached office on a lot with a main dwelling an accessory structure? Label it a cabana or pool house, same thing, as long as not designed, built, or intended for living. I'm sure zoning ordinances and hoa rules treat this differently but I was addressing just the IRC.
Well I'm longing for the fantastic canoe routes of the truley great white north now but are you saying a garage over 660 sf has to have a full foundation where you live?Limit for small garages not being on a full foundation is 660 sq. ft. in the Great White North as well.
Always interesting to see the consistency between our two codes.
I agree with all of this except the last paragraph. There must be moisture in the soil but not necessarily water. You also need clay in the soil to create the lensing which is what drives the force exerted in frost heave. You can certainly have frost heave below buildings with clay soils and all other water management done correctly.My understanding of the "why" it is allowed for a garage up to 600 Sq. Ft. is not that the building will not be subject to frost heave, it absolutely will (well, depending on your soils and temperatures), it is allowed because there is unlikely to be differential movement in the structure due to the small size. Even if there is an issue, because it is "only" a garage, it is unlikely to become a life safety issue or damage the structure to the point it is unable to be used for it's intended purpose. Basically, the risk assessment allows it.
This isn't to say that it is a good idea to do this everywhere, it is a minimum code after all. Certainly, if you have an area with vastly different soil types, you might want to ensure the foundation is below frost.
While there are sometimes where frost will come in underneath a garage slab that is independent of the building foundation and cause it to heave, it is relatively unlikely. Remember, for frost to heave the ground, there has to be water in it. The only way that the ground is going to have water in it with a building overtop is either really poor water management, or soil particles that are small enough to engage capillary action and hold water instead of letting it drain away.
You're reading words and not definitions. Frost protection is required for structures, slabs are not defined as such unless they are elevated.I'm trying to focus on what the IRC requires, not what I'd require or what makes sense or what some people believe the IRC requires but can't quite point to it.
As far as the driveway, if it were a load scheduled in R301 that R401.2 said had to be "accomodated" and thus supported by a frost protected foundation, I would say the code says yes. But all "passenger vehicle garages" are scheduled and no concrete driveway nor dirt nor any driveways are scheduled. As pointed out there are exceptions to the frost ptotection requirement but none apply to a >600 sf garage. I'm just reading the words in the IRC.
Rick, my family is from Montrose PA area, great grandfather settled there I 1840, and we almost moved there for retirement.In PA you can build a garage up to 2,000 sq ft without a permit. And not need frost protection. This doesn't mean it's a good idea to do it.
What "moisture" are you seeing that is not water?I agree with all of this except the last paragraph. There must be moisture in the soil but not necessarily water. You also need clay in the soil to create the lensing which is what drives the force exerted in frost heave. You can certainly have frost heave below buildings with clay soils and all other water management done correctly.
To a different post, frost doesn't like or dislike anything, it's all simple thermodynamics. The only barrier to heat moving through a stem wall is the very little insulating properties it has. What you're actually seeing when there is no frost under a floating slab is the insulation of the structure above it reducing the heat radiating up. The roof is helping you, the stem wall is negligible.
Sorry, Typo. 600 Sq. Ft. and yes they have some sort of full foundation under them. Typically we see a frost wall, just a 4' wall with footings to get them below the frost line, but we have people provide an engineered design for a slab on occasion as well.Well I'm longing for the fantastic canoe routes of the truley great white north now but are you saying a garage over 660 sf has to have a full foundation where you live?
I need to look more at IBC and type U buildings perhaps, treating a 1000 sf building for vehicles as something other than an accessory structure to an IRC dwelling. Or just submit for permit and assume (safely I'm sure) reviewer will not care the 1000 sf garage floor is not supported on a frost protected foundation.