smoke alarm in kitchen
Mr. Inspector
Poconos/eastern PA
Most houses here are small vacation homes. They have two bedrooms upstairs with a balcony over a great room with a catheral cieling. No basement. Master bed room is on 1st floor off kitchen. Where are they suppose to put the smoke alarm? The home is only 38' x 20'. If you put the smoke alarm 10' away from kitchen it ends up on the far side of the house from the bedroom by the gas fireplace. And you would have to put it outside on the deck to get 20' from the stove.
Installing a photoelectric smoke alarm instead of an ionization smoke alarm may be one approach to reducing nuisance alarms.
photoelectric smoke alarms are less prone to nuisance alarms in the kitchen area than ionization smoke alarms
From the `06 IRC, Section R313.2 - Smoke Alarms, # 2: "outside
each separate sleeping area in the immediate vicinity of the bedrooms".
Installation of an approved type Smoke Alarm may be a trial & error
process in your case **Rick**, to find the most workable & compliant
location.
Without seeing a floor plan hard to give a good answer
With that said one in each bedroom
One "somewhere" outside
Not sure about your distances
But would say technically a smoke alarm covers 15 feet on each side
So as stated above maybe trail and error
I would not worry to much about the upstairs one
Does the upstairs bedrooms have doors to them??
And the one for the master bedroom to me can be max fifteen feet from the door to the bedroom
This is what bugs me about the requirements, say you had a very large house the way ideas the code you only need one on say the first level, if it did not have any bedrooms.
Does a one require them to be spaced for coverage, in that there would be a few detectors on that first level with very large sq ft
I think the whole idea for alarms is wake people in the bedrooms. So what's more important, the alarm close to the bedroom in the kitchen or 25' away on the other end of this house.
In your case near the bedroom door
But does no hood if cooking constantly sets it off
So I would look where I could put it up to fifteen feet away from the bedroom door in order to cut down on false alarms and the home owner just taking it down
Maybe on the upstairs put them on the wall above the bedroom doors, installed properly.
That should get them as far from the kitchen as possible, plus they are not on the ceiling
Code still allows the SD to be placed on the wall, would that help? I would'nt think steam from cooking in the kitchen would set the alarm off if mounted on the wall. In my home the SD would go off due to a header trapping steam, so the wall mount idea may work.
pc1
I remeber something about 20' from cooking appliance.It is in the Manufactures installation instructions or NFPA 72 that is referenced by the code.
2007 NFPA 72 11.8.3.5(4) Smoke alarms and smoke detectors installed within a 6.1m (20 ft) horizontal path of a cooking appliance shall be equiped with an alarm-silecing means or be of the photoelectric type.
Well you learn something new every day!!!!
Love this job
UPDATE::::
2010 and 2013
29.8.3.4 Specific Location Requirements. The installation of smoke alarms and smoke detectors shall comply with the following requirements:
(4)*
Smoke alarms and smoke detectors shall not be installed within an area of exclusion determined by a 10 ft (3.0 m) radial distance along a horizontal flow path from a stationary or fixed cooking appliance, unless listed for installation in close proximity to cooking appliances. Smoke alarms and smoke detectors installed between 10 ft (3.0 m) and 20 ft (6.1 m) along a horizontal flow path from a stationary or fixed cooking appliance shall be equipped with an alarm-silencing means or use photoelectric detection.
Exception: Smoke alarms or smoke detectors that use photoelectric detection shall be permitted for installation at a radial distance greater than 6 ft (1.8 m) from any stationary or fixed cooking appliance when the following conditions are met:
(a)
The kitchen or cooking area and adjacent spaces have no clear interior partitions or headers and
(b)
The 10 ft (3.0 m) area of exclusion would prohibit the placement of a smoke alarm or smoke detector required by other sections of this code.
(5)
Effective January 1, 2016, smoke alarms and smoke detectors used in household fire alarm systems installed between 6 ft (1.8 m) and 20 ft (6.1 m) along a horizontal flow path from a stationary or fixed cooking appliance shall be listed for resistance to common nuisance sources from cooking.