• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Smoke and Draft Control IBC 2009

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,076
Location
Somewhere Too Hot & Humid
Exception 4 of Section 708.4.1 is applied to a 3-story Group R1/R2 building. The building is protected throughout with an automatic sprinkler system and the corridors have a ½ fire-resistance rating. Hence, an enclosed elevator lobby is not required. Is the elevator shaft enclosure door opening required to comply with the smoke and draft control requirements for a door assembly in a corridor of Section 715.4.3.1 when opening into the fire-resistance rated corridor?
 
This is a case where you typically see the "flop doors" over the elevator door. Elevator doors cannot be smoke and draft controll.
 
1. I believe the section is 708.14.1 and not 708.4.1.

2. I don't believe the intent was to replace the lobby with a smoke-control door. Per the Commentary regarding this exception: "This recognizes the effectivenessof sprinkler systems in controlling thespread of smoke."

3. Elevator lobbies are only required when the elevator connects more than three stories--your example is only a three-story building.
 
This is a common question. A strict interpretation would concur with Coug Dad, that the exception for not requiring elevator lobbies does not eliminate the requirement to protect openings into a fire-resistance-rated corridor with S-labeled doors per UL 1784 in accordance with 715.4.3.1.

As the elevator hoistway doors are not S-labeled, we could conclude that additional protection is required.

You could also use something like the SmokeGuard M1500 to create a lobby without protecting each hoistway opening.
 