thanks getting closer
nfpa 90a
1.1* Scope.This standard shall cover construction, installation, operation, and maintenance of systems for air conditioning and ventilating, including filters, ducts, and related equipment, to protect life and property from fire, smoke, and gases resulting from fire or from conditions having manifestations similar to fire.
from nfpa 80
does 80 apply to smoke evac systems??
1.2.1 The purpose of this document is to set national standards for the installation and maintenance of assemblies used to protect openings in walls, floors, and ceilings to prevent or retard the spread of fire and smoke within, into, or out of buildings.
1.2.2 This document is also intended to give guidance to authorities having jurisdiction (AHJs) so they can determine in the field if an assembly meets the requirements and standards outlined in this document and if maintenance standards have been maintained.
1.2.3* It is not the purpose of this standard to establish the degree of protection required or to constitute the approval of any product.
Chapter 19 Installation Testing Maintenance Fire Dampers
19.4* Periodic Inspection and Testing.
19.4.1 Each damper shall be tested and inspected 1 year after installation.
19.4.1.1 The test and inspection frequency shall then be every 4 years, except in hospitals, where the frequency shall be every 6 years.
19.4.2 All tests shall be completed in a safe manner by personnel wearing personal protective equipment.
19.4.3 Full unobstructed access to the fire or combination fire/smoke damper shall be verified and corrected as required.
19.4.4 If the damper is equipped with a fusible link, the link shall be removed for testing to ensure full closure and lock-in-place if so equipped.
19.4.5 The operational test of the damper shall verify that there is no damper interference due to rusted, bent, misaligned, or damaged frame or blades, or defective hinges or other moving parts.
19.4.6 The damper frame shall not be penetrated by any foreign objects that would affect fire damper operations.
19.4.7 The damper shall not be blocked from closure in any way.
19.4.8 The fusible link shall be reinstalled after testing is complete.
19.4.8.1 If the link is damaged or painted, it shall be replaced with a link of the same size, temperature, and load rating.
19.4.9 All inspections and testing shall be documented, indicating the location of the fire damper or combination fire/smoke damper, date of inspection, name of inspector, and deficiencies discovered.
19.4.9.1 The documentation shall have a space to indicate when and how the deficiencies were corrected.
19.4.10 All documentation shall be maintained and made available for review by the AHJ.
19.4.11 Periodic inspections and testing of a combination fire/smoke damper shall also meet the inspection and testing requirements contained in Chapter 6 of NFPA 105, Standard for Smoke Door Assemblies and Other Opening Protectives.
still can not access nfpa 90 on the paid side