Smoke Partition vs construction capable of resisting the passage of smoke

Tim Mailloux

REGISTERED
Joined
Feb 12, 2018
Messages
918
Location
Hartford CT
Section 509.4.2 (Incidental Use) Protection states where the code permits an automatic sprinkler system without a fire barrier, the incidental uses shall be separated from the remainder of the building by ‘construction capable of resisting the passage of smoke’. The description given for ‘construction capable of resisting the passage of smoke’ in 509.4.2 is very similar to that of a Smoke Partition in section 710. What is the difference between the two?
 
The construction capable of resisting the passage of smoke must meet the requirements described following that comment. It is not required to meet the requirements of section 710, which get a little more specific.
 
The construction capable of resisting the passage of smoke must meet the requirements described following that comment. It is not required to meet the requirements of section 710, which get a little more specific.
the requirments are so close to one another that Imnot sure why the ICC even bothered.
 
I, too, am puzzled by the language used for incidental uses since a smoke partition has been in the IBC for nearly twenty years. What I have done for situations where a sprinkler system is permitted in lieu of fire barriers, I use smoke partitions because they achieve the same result and are easier to describe on a set of drawings. I have had no pushback from plans examiners when I have done this (as a matter of fact, I describe this in my book).

When incidental uses were introduced with the 2000 IBC, there was no smoke partition assembly, so they used a descriptive/performance requirement. The smoke partition was added in the 2003 IBC to easily describe the corridor walls used for Group I-2. However, it has never been picked up to describe walls for incidental uses.

There are several things I would like to change in the IBC and other codes but I have not had the time or inclination to dive into cdpAccess to propose changes. Now that I have been more involved in the current code development this cycle, I plan on making several changes during the next code cycle, and this situation will be one of those proposals.
 
The so-called "smoke partition" is actually a heat trapping partition, to keep the hot air rising from a fire within the room so it will set off the sprinkler head.
 