smoke vents..

Marshal Chris

Silver Member
Joined
Oct 23, 2009
Messages
155
Location
Long Island, NY
Hello all,

Looking at taking the ICC Fire Inspector 2 Test. A question posed was this:

Using a commodity Class III and having a S-1, Option 1, a building that is 240 feet x 480 feet ; Curtain board depth is 6 feet; and storage height is 30 feet. Answer the following: What is the total number of vents required?

A. 5

B. 6

C. 7

D. 8

I'm having difficulty of this, can anyone lend a hand in figuring this out?
 
Is there a problem with the question?

Sq ft is 115,200

Looks like the ratio is 1/75
 
My guess is they are asking about the number of vents per draft curtain area. So, with a 8,000SF/75=106.67SF total vent area per draft curtain area.

Then I guess you're supposed to assume the minimum size vent (4'x4') which would mean 106.67SF/16SF per vent=6.67 vents, so round up to 7 vents required.

Lucky thing it wasn't fill in the blank, I'd have gotten it wrong since the question was worded so poorly relative to the answer they wanted.
 
AegisFPE said:
My guess is they are asking about the number of vents per draft curtain area. So, with a 8,000SF/75=106.67SF total vent area per draft curtain area.Then I guess you're supposed to assume the minimum size vent (4'x4') which would mean 106.67SF/16SF per vent=6.67 vents, so round up to 7 vents required.

Lucky thing it wasn't fill in the blank, I'd have gotten it wrong since the question was worded so poorly relative to the answer they wanted.
Very good

Not a math type person
 
Based on the building area, storage height and commodity classification, IFC Table 2306.2 doesn't require draft curtains for high-piled combustible storage. Just one more problem with this question.
 
Oldfieldguy said:
Based on the building area, storage height and commodity classification, IFC Table 2306.2 doesn't require draft curtains for high-piled combustible storage. Just one more problem with this question.
Correct again, did not read all the way across
 
Thank you! Their answer was 7 and I didn't know how they had arrived at that! Thanks again!

AegisFPE said:
My guess is they are asking about the number of vents per draft curtain area. So, with a 8,000SF/75=106.67SF total vent area per draft curtain area.Then I guess you're supposed to assume the minimum size vent (4'x4') which would mean 106.67SF/16SF per vent=6.67 vents, so round up to 7 vents required.

Lucky thing it wasn't fill in the blank, I'd have gotten it wrong since the question was worded so poorly relative to the answer they wanted.
 
Marshal Chris said:
Thank you! Their answer was 7 and I didn't know how they had arrived at that! Thanks again!
Where did the question come from???

Icc test

Another study guide??

???
 
Marshal Chris said:
I googled ICC fire inspector 2 test. I think the one i was looknig at was for north carolina. I was looking at questions to guage my readiness.
Sounds like you are ready;;; answer E to all questions

E. question does not make any sense
 