G2arch
Member
I have a project with two suites for a Husband (Psychologist) and Wife (Dentist). This project in under IBC2012. Building is type IIB and Non-sprinkled. Psych suite is 1135sf (12 occupants) and and Dental suite is 1790sf (18 occupants). (30occupants total) As individual Suites they qualify as spaces with one means of Egress per Section 1015.1. The issue is they want to put a door from the Psych suite into the lounge of the Dental Suite. (Top center part of Plan). When we do this does my two suites become a single Space in lieu of two individual spaces? I can not find the definition of space in the code book. If the interpretation is that the Suites are one Space because of the door, are any of the following possible solutions;A. Delete the door (obvious solution but not desired by owner)B. Rate the wall between Suites.C. Add a door between the waiting rooms so that the common path from anywhere in the two suites to just one of the two suite entry doors is less than 100ft. Thus, the entire combined suites would qualify per Section 1015.1. We would want to keep both doors but only one would be required. This seems to meet code but seems like the addition of this door does not really increase life safety as exiting directly through a suite entry door would be quicker in both cases.