2009 IFC section 3403.4 says secondary containment is required where the MAQ is exceeded AND when required by 2704.2.
I have a building that wants an indoor tank to store 240 gallons of kerosene to be used in a power washer power. The buidling is sprinklered. MAQ for class II is 120 double for sprinkler is 240.
Since the individual contain is over 55 gallons but this ammount is not over the MAQ, and section 3403.4 says it has to be over the MAQ "AND" when required by 2704.2, (not "OR"), then secondary containment and spill control is not required. Because of the "and" instead of "or", both conditions must be met so this would not require secondary containment.
Q: I'm a reading this right? No secondary containment or spill control even though the container is over 55 gallons- because in doesn't exceed the MAQ.
Q: Is a dispensing by gravity okay?
I have a building that wants an indoor tank to store 240 gallons of kerosene to be used in a power washer power. The buidling is sprinklered. MAQ for class II is 120 double for sprinkler is 240.
Since the individual contain is over 55 gallons but this ammount is not over the MAQ, and section 3403.4 says it has to be over the MAQ "AND" when required by 2704.2, (not "OR"), then secondary containment and spill control is not required. Because of the "and" instead of "or", both conditions must be met so this would not require secondary containment.