Given:
A set of plans for a commercial space proposes a spiral staircase. 2018 IBC 1011.1 requires a handrail on both sides of every flight of stairs. Exception #1 allows for a handrail on one side only for spiral stairways. And NFPA 101 Life Safety Code section 7.2.2.2.3 requires handrails on both sides of spiral stairs. Can anyone tell me if there is an exception granted by the Life Safety Code that would allow the inside handrail to be eliminated? Again I say that this is a commercial space.
As always, thanks in advance.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
A set of plans for a commercial space proposes a spiral staircase. 2018 IBC 1011.1 requires a handrail on both sides of every flight of stairs. Exception #1 allows for a handrail on one side only for spiral stairways. And NFPA 101 Life Safety Code section 7.2.2.2.3 requires handrails on both sides of spiral stairs. Can anyone tell me if there is an exception granted by the Life Safety Code that would allow the inside handrail to be eliminated? Again I say that this is a commercial space.
As always, thanks in advance.