Spot the violations: Electrical 2

jar546

CBO
Joined
Oct 16, 2009
Messages
12,996
Location
Not where I really want to be
There are more than 1 here too:

IMG_5838.JPG
 
Terminal not listed for 2 conductors.

Is the line on the right the a grounding or groundedl?
 
Grounds are dissimilar metals together on a terminal designed for one conductor?

Panel cover missing! He He!

pc1
 
I see it now, dbrown, you are good!

Do you make them put colored tape on the conductor ends?

pc1
 
Pcinspector1 said:
I see it now, dbrown, you are good! Do you make them put colored tape on the conductor ends?

pc1
What code section requires colored tape to be installed on the ends of the conductors of a residential feeder?

Chris
 
raider1 said:
What code section requires colored tape to be installed on the ends of the conductors of a residential feeder?Chris
Where did anyone state this was a resi feeder?
 
Concuctors not phased, lug rated for 1 conductor, need plastic bushing on load side connector and if it's a metal conduit a bonding bushing would be required.
 
I see the white line on the GC but I was not aware that this was a residential application. It makes sense that it is being a 200amp set-up.

I did'nt state a code requirement for tape, I only asked a question if it's required?

Look, I'm just trying to learn here and I always try to thank someone that helps me.
 
Jim Harper said:
Concuctors not phased, lug rated for 1 conductor, need plastic bushing on load side connector and if it's a metal conduit a bonding bushing would be required.
fatboy said:
Missing a bushing on the nipple entering the bottom of the box.
The bottom connector would most likely be a cable clamp and not a conduit connector therefore a bushing is not required.

The requirement for phaseing the conductors by phase and system only applies if the building has more than one nominal voltage system. If this is indeed a residential application then 210.5 © would not apply and the ungrounded conductors are not required to be identified.

Chris
 
Pcinspector1 said:
I see the white line on the GC but I was not aware that this was a residential application. It makes sense that it is being a 200amp set-up.I did'nt state a code requirement for tape, I only asked a question if it's required?

Look, I'm just trying to learn here and I always try to thank someone that helps me.
I apologize if I came across harsh, I did not intent too. :)

Again the requirement to identify the ungrounded conductors by phase is only required if the building is supplied by more than 1 nominal voltage system.

Chris
 
NEC Definition of Feeder:All circuit conductors between the service equipment, the sorce of a separatetly derived system, or other power supply source and the final branch-circuit overcurrent device. With that definition of Feeder, would not section E3307 apply?
 
Sorry, I also assumed, thought it looked like a nipple for conduit termination. And took to long posting Jim H. beat me to it.
 
Kevin Turner said:
NEC Definition of Feeder:All circuit conductors between the service equipment, the sorce of a separatetly derived system, or other power supply source and the final branch-circuit overcurrent device. With that definition of Feeder, would not section E3307 apply?
E3407.3 (2009 IRC) states that the insulation on Ungrounded conductors shall be a continious color other than white, gray or green. Both ungrounded conductors are black and meet the requirements of this section. There is nothing in E3407.3 that requires the ungrounded conductors to be identifed by phase.

Chris
 