Spot the violations: Electrical1

jar546

CBO
Joined
Oct 16, 2009
Messages
12,997
Location
Not where I really want to be
How many violations could you write up on this installation:

IMG_2892.JPG
 
Gonna give it a quick quess:

1.Securing NM cable within 12" of box

2. NM cable pasing thru another panelboard

3. Re-identifying white conductors used as ungrounded

4. 3 NM cables under 1 romex connector?

What else am I missing?
 
1.Securing NM cable within 12" of box - NEC 334.30 IRC TAble E3702.1 2003 Edition

2. NM cable pasing thru another panelboard - NEC 312.8 is pushing it, but not sure what else would apply IRC Reference unknown

3. Re-identifying white conductors used as ungrounded - NEC 200.7 ©(1) IRC E3307.3 Exception 2003 Edition

4. 3 NM cables under 1 romex connector? - Manufacturers listing (NEC 110.3 (B)) IRC E3303.3 2003 Edition
 