Mixed Use, Separated Building w/ basement
A 3,000 sq ft daycare occupancy (Group E) will be located on the first floor, which is the level of exit discharge.
[F] 903.2.3 Group E. An automatic sprinkler system shall be provided for Group E occupancies as follows:
1. Throughout all Group E fire areas greater than 12,000 square feet (1115 m2) in area.
2. Throughout every portion of educational buildings below the lowest level of exit discharge serving that portion of the building.
Exception: An automatic sprinkler system is not required in any area below the lowest level of exit discharge serving that area where every classroom throughout the building has at least one exterior exit door at ground level.
The basement is storage. Does the basement need to be sprinklered? It is below the lowest level of exit discharge, but it is not part of the Daycare occupancy. Not every classroom will have an exterior exit door at ground level, so the exception would not apply.
Thanks in advance.
Mixed Use, Separated Building w/ basement
A 3,000 sq ft daycare occupancy (Group E) will be located on the first floor, which is the level of exit discharge.
[F] 903.2.3 Group E. An automatic sprinkler system shall be provided for Group E occupancies as follows:
1. Throughout all Group E fire areas greater than 12,000 square feet (1115 m2) in area.
2. Throughout every portion of educational buildings below the lowest level of exit discharge serving that portion of the building.
Exception: An automatic sprinkler system is not required in any area below the lowest level of exit discharge serving that area where every classroom throughout the building has at least one exterior exit door at ground level.
The basement is storage. Does the basement need to be sprinklered? It is below the lowest level of exit discharge, but it is not part of the Daycare occupancy. Not every classroom will have an exterior exit door at ground level, so the exception would not apply.
Thanks in advance.