Sprinkler heads in walkin coolers?
mtlogcabin
Big Sky Country
Was there ever a time frame when sprinkler coverage was not required for walk-in coolers? Maybe under the UFC or NFPA
I have been reviewing annual sprinkler reports and noticed a lot of walk-in coolers do not have coverage. The buildings where constructed under the Uniform building and fire codes. I don't want to require a correction if it was not required at the time of construction. It would have been an easy miss in those days since the FD signed off on sprinklers and the personnel back then had little training in sprinkler coverage requirements.
Only one I remember was vaults
Would have to look at an old nfpa 13, but I don't think there is an exception there.
NFPA 101-2000 edition or NFPA 13 1999 Edition
NFPA 13, Standard for the Installation of Sprinkler Systems, 1999 Edition requires a building, where protected by an automatic sprinkler system, to be provided with sprinklers in all areas [NFPA 13, §1-6]. Exceptions to sprinkler installation in all areas apply where specific sections of NFPA 101-2000 edition or NFPA 13 permit the omission of sprinklers or providing alternate extinguishing systems.
remember this is OLD code Therefore,under these codes
alternative suppression systems approved by the Authority Having Jurisdiction can be used
Oldest NFPA 13(Actually National Board of Fire Underwriters) I have is 1953 don't see exception there
cda said:
Ice cream does not burn
Photo+May+16%252C+2013%252C+1%253A47+AM