13R
Chapter 6 Installation
6.6 Location of Sprinklers.
6.6.1 Sprinklers shall be installed in all areas except where omission is permitted by 6.6.2 through 6.6.7.
6.6.2* Sprinklers shall not be required in bathrooms where the bathroom area does not exceed 55 ft2 (5.1 m2).
6.6.3 Except where specified in 6.6.4, sprinklers shall not be required in clothes closets, linen closets, and pantries within dwelling units that meet all of the following conditions:
(1)
The area of the space does not exceed 24 ft2 (2.2 m2).
(2)
The least dimension does not exceed 3 ft (0.91 m).
(3)
The walls and ceilings are surfaced with noncombustible or limited-combustible materials as defined by NFPA 220.
6.6.4* Sprinklers shall be installed in any closet used for heating or air-conditioning equipment, washers, dryers, or water heaters except as permitted by 6.6.7.
6.6.5* Except as provided for in 6.6.5.1, sprinklers shall not be required in any porches, balconies, corridors, carports, porte cocheres, and stairs that are open and attached.
6.6.5.1 Where a roof or deck is provided above, sprinklers shall be installed to protect attached exterior balconies, attached exterior decks, and ground floor patios serving dwelling units in buildings of Construction Type V.
6.6.5.1.1 Where sidewall sprinklers are installed beneath decks or balconies constructed with open wood joists, sprinklers shall be permitted to be installed with deflectors not less than 1 in. (25 mm) or more than 6 in. (152 mm) below the structural members, provided that the deflector is not more than 14 in. (356 mm) below the underside surface of the deck.
6.6.6* Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling unit ventilation equipment, crawl spaces, floor/ceiling spaces, noncombustible elevator shafts where the elevator cars comply with ANSI A17.1, Safety Code for Elevators and Escalators, and other concealed spaces that are not used or intended for living purposes or storage and do not contain fuel-fired equipment.
6.6.6.1 When fuel-fired equipment is present, at least one quick-response intermediate temperature sprinkler shall be installed above the equipment.
6.6.7 Sprinklers shall not be required in closets (regardless of size) on exterior balconies and exterior breezeways/corridors, regardless of size, as long as the closet does not have doors or unprotected penetrations directly into the dwelling unit.
6.6.8 All situations regarding sprinkler location and position that are not directly discussed in NFPA 13R shall be in accordance with NFPA 13.
6.6.9 Interior Stairwells.
6.6.9.1 Except as allowed by 6.6.9.2, 6.6.9.3, and 6.6.9.4, sprinklers shall be installed throughout all interior, enclosed stairwells.
6.6.9.2* Sprinklers shall not be required underneath stair risers in dwelling units where the walls and ceilings are surfaced with noncombustible or limited-combustible finishes.
6.6.9.3 Closets located underneath stairs shall be protected in accordance with 6.4.6.3.2, 6.6.3, 6.6.4, and 6.6.7.
6.6.9.4 Interior stairwells located outside the dwelling unit shall be protected in accordance with NFPA 13.