Marshal Chris
Silver Member
Hello all!
I have done an inspection in a adult community recently and uncovered a situation that I'm looking for some assistance. This particular building was constructed around 2000 and built to the NY "Green Book" code. During the inspection, we noticed a concealer cover plate that was different than the rest, so I checked it for compatibility with the head. It wasn't and I found it to be a standard response head (G4) but it was in the kitchen, so I decided to check a few heads in the dining room. I found them to be G4FR. I am almost positive these heads were never listed as a quick response head but a co-worker found some exceptions with regards to a fast response element of a certain RTI. I haven't been able to find any documentation about the RTI.
Does anyone know if this was allowed then? Thoughts?
Thanks!
Chris
I have done an inspection in a adult community recently and uncovered a situation that I'm looking for some assistance. This particular building was constructed around 2000 and built to the NY "Green Book" code. During the inspection, we noticed a concealer cover plate that was different than the rest, so I checked it for compatibility with the head. It wasn't and I found it to be a standard response head (G4) but it was in the kitchen, so I decided to check a few heads in the dining room. I found them to be G4FR. I am almost positive these heads were never listed as a quick response head but a co-worker found some exceptions with regards to a fast response element of a certain RTI. I haven't been able to find any documentation about the RTI.
Does anyone know if this was allowed then? Thoughts?
Thanks!